Building residential house Disconnect

Status
Not open for further replies.

bluecollar84

Senior Member
Location
US
What does the code say about needing a disconnect at the meter socket if the panel inside the house is not within So many feet of the point of Entry of a basement ? Code article please ? Thanks


Sent from my iPhone using Tapatalk
 
What does the code say about needing a disconnect at the meter socket if the panel inside the house is not within So many feet of the point of Entry of a basement ? Code article please ?

The Code won't help as it doesn't specify an actual distance.

In my work areas, the AHJs and the PoCo have agreed upon a maximum distance, and how it is measured.
 
The rationale is to minimize the length of wire not effectively protected by OCPD inside the house. What makes the difference is the OCPD required to be associated with the service disconnect, not the disconnect itself.

Sent from my XT1585 using Tapatalk
 