A client has a 4160 volt service. That supplies 4 or 5 transformers scattered around the building. Each transformer supplies 208 volts to separate main switchboards inside the building, and each switchboard has a 2000 amp main breaker.
I have a couple of questions regarding the feeders between each transformer and its main switchboard.
1. Can these be 4 wire feeders? As in 3 hot wires and a grounded service conductor? This is how they would be installed if they were service conductors. (i.e. - If the power company owned the transformers, and the services were 208 volts.) However, I believe I've heard this may not be allowed for customers owned transformers.
2. Can these be 5 wire feeders? Then we would have 3 hot wires, a neutral, and a ground from each transformer to each switchboard.
3. If they are 5 wire feeders, where should the bonding between neutral and ground occur? In the transformer, or in the switchboard? Both the transformer and the switchboard are shipped with a bonding jumper installed between the neutral connection and the ground connection. I assume one of these would have to be removed.