Building steel as grounding electrode

Status
Not open for further replies.

cppoly

Senior Member
Location
New York
In an article from Mike Holt, he says "The 2011 NEC no longer allows the structural metal to serve as a grounding electrode when supplemented by a ground rod."

This doesn't make sense, does it? I thought when multiple electrodes were present they all have to be bonded together, so why would building steel not be allowed to be used an electrode if connected to a ground rod?
 
In an article from Mike Holt, he says "The 2011 NEC no longer allows the structural metal to serve as a grounding electrode when supplemented by a ground rod."

This doesn't make sense, does it? I thought when multiple electrodes were present they all have to be bonded together, so why would building steel not be allowed to be used an electrode if connected to a ground rod?

Not to speak for MH, but maybe I can clarify.

The structural metal frame is not an electrode, only the part that is in the ground for 10'.

One may attach a GEC to the frame as long as part of that frame eventually qualifies as an electrode or is attached to a CEE.

You can not attach a GEC to a frame that is only supplemented by a ground rod. Basically in order to use the frame to extend the GEC to a ground rod or such, part of that frame has to qualify as an electrode or be properly attached to a concrete encased electrode, not just a rod or such.
 