I just ran across a PDF from our POCO, Consumers Energy, that has wiring diagrams and all sorts of cool stuff in it.
http://www.consumersenergy.com/uplo...Service-Metering-Information-Requirements.pdf
If you look at page 61 you will find their wiring requirements for transfer switches. It appears that they consider the transfer switch the point of the first disconnect as that is where the neutral/ground bonding is done.
So, how many of you move the bonding point from the customer's main breaker panel to the inside of the transfer switch box when you install a transfer switch?
Also, take note that the drawings also require that the neutral NOT be switched.
Now, what's odd is that I have seen inspectors require a switched neutral but never a bonding relocation.
As soon as I can find my inspector pal's e-mail address I will forward the PDF to him and solicit his comments, but 'till then, I would really like some feed back from the Holtizens.
Thanks!
http://www.consumersenergy.com/uplo...Service-Metering-Information-Requirements.pdf
If you look at page 61 you will find their wiring requirements for transfer switches. It appears that they consider the transfer switch the point of the first disconnect as that is where the neutral/ground bonding is done.
So, how many of you move the bonding point from the customer's main breaker panel to the inside of the transfer switch box when you install a transfer switch?
Also, take note that the drawings also require that the neutral NOT be switched.
Now, what's odd is that I have seen inspectors require a switched neutral but never a bonding relocation.
As soon as I can find my inspector pal's e-mail address I will forward the PDF to him and solicit his comments, but 'till then, I would really like some feed back from the Holtizens.
Thanks!