Bundeling M.C

Status
Not open for further replies.

Big Guns

Member
What article is bundeling MC under, I need to know how many MCs I can bundle together above a ceiling with tie wire. I checked article 310 also installation of MC, I cant find it but Ive seen it before.
 
Art. 310.15(B)(2)exception 5

310.15(B)(2) Adjustment Factors.
(a) More Than Three Current-Carrying Conductors in a Raceway or Cable. Where the number of current-carrying conductors in a raceway or cable exceeds three, or where single conductors or multiconductor cables are installed without maintaining spacing for a continuous length longer than 600 mm (24 in.) and are not installed in raceways, the allowable ampacity of each conductor shall be reduced as shown in Table 310.15(B)
Exception No. 5: Adjustment factors shall not apply to Type AC cable or to Type MC cable without an overall outer jacket under the following conditions:
(1) Each cable has not more than three current-carrying conductors.
(2) The conductors are 12 AWG copper.
(3) Not more than 20 current-carrying conductors are bundled, stacked, or supported on ?bridle rings.?
 
Status
Not open for further replies.
Top