The inspector at our job site called us on bundling some home runs going through a wall. The runs are supported by UL listed j-hooks suspended by all-thread. Due to the length of these circuits, we’ve had to upsize our home runs up to 6 awg for 20A. In the 2020 NEC, it says in 310.15 (C) (1) (d) (1-4),
(d) Adjustment factors shall not apply to Type AC Cable or to Type MC Cable under the following conditions:
(1) The cables do not have an overall outer jacket.
(2) Each cable has not more than three current-carrying conductors.
(3) The conductors are 12awg copper.
(4) Not more than 20 current-carrying conductors are installed without maintaining spacing, are stacked, or are supported on “bridle rings.”
We meet the requirements of 1 and 2. The exception for 4 says for more than 20 current-carrying conductors longer than 24 in. a 60% adjustment factor shall be applied. With 1,2 and 4 met, that leaves 3 up to question. It’s not 12awg because it’s adjusted to voltage drop. Is there another code reference I am missing? Is bundling in our case permitted?
(d) Adjustment factors shall not apply to Type AC Cable or to Type MC Cable under the following conditions:
(1) The cables do not have an overall outer jacket.
(2) Each cable has not more than three current-carrying conductors.
(3) The conductors are 12awg copper.
(4) Not more than 20 current-carrying conductors are installed without maintaining spacing, are stacked, or are supported on “bridle rings.”
We meet the requirements of 1 and 2. The exception for 4 says for more than 20 current-carrying conductors longer than 24 in. a 60% adjustment factor shall be applied. With 1,2 and 4 met, that leaves 3 up to question. It’s not 12awg because it’s adjusted to voltage drop. Is there another code reference I am missing? Is bundling in our case permitted?