scottam99
Member
- Location
- Vero Beach Florida
I am reading the exception 315 (B) 2a Exception # 5. It states that Adjustment factors shall not apply if each cable has no more than 3 current carrying conductors.
Am I right to assume that if I am installing 12-3-3 ( 3 hots, 3 neutrals in each MC cable) i have to derate no matter what? So If I install 2 of this type MC I already have 12 Current carrying conductors. I would have to increase wire size to number 10's?
Additionally I would have to derate if I am using #10-3-3 ( 3 hots, 3 neutrals in each cable ) for voltage drop no matter how many cables I am installing?
Am I right to assume that if I am installing 12-3-3 ( 3 hots, 3 neutrals in each MC cable) i have to derate no matter what? So If I install 2 of this type MC I already have 12 Current carrying conductors. I would have to increase wire size to number 10's?
Additionally I would have to derate if I am using #10-3-3 ( 3 hots, 3 neutrals in each cable ) for voltage drop no matter how many cables I am installing?