334.80 ... Where more than two NM cables containing two or more current-carrying conductors are bundled together and pass through wood framing that is to be fire- or draftstopped using thermal insulation or sealing foam, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a). [ROP 7?150a]
Could have sworn it was electricity that ran through wires in the wall...Originally posted by channing123:
there is a certain thing called temperature and it runs through wires common sense unless you figure to never turn power on
Good question!Originally posted by macmikeman:
Has there been any real field testing done to determine if multiple romex cables passing thru a single hole in a residential setting actually needs derating or is this just because too many people with word processors bounced the concept around soo much that it has become such an issue it finally made it into the code book?
334.80 Ampacity. The ampacity of types NM, NMC, and
NMS cable shall be determined in accordance with 310.15.
The ampacity shall be in accordance with the 60 degree C (140 F)
conductor temperature rating. The 90 C (194 F) rating
shall be permitted for ampacity derating purposes,
provided the final derated ampacity does not exceed
that for a 60 C (140 F) rated conductor.