Two cables zip ties together are bundled. As Augie stated after 4 cables the derating will lower the 20 amp rating associated with #12 AWG.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Just a quick note that the previous answers assume a 30C or less ambient temperature. If bundling occurs in a higher ambient temperature (say a typical unconditioned residential attic), then bundling can cause significant derating with fewer than (5) 12-2 cables.

Cheers, Wayne
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
Because that is 10 CCC'S which requires a derating to 50%.

30*50%=15 amps no good for 20 amps.

9 CCC'S would be 30*70%=21 amps good for a 20 amp circuit.
I see that now. I didn't understand Gus' reply at first. my initial thought was what you said in your post. Two cables would be bundling as you would have (4) CCC
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I see that now. I didn't understand Gus' reply at first. my initial thought was what you said in your post. Two cables would be bundling as you would have (4) CCC
Yeah Gus just gave us a shortcut to the no more than 9 CCC'S rule of thumb for #12 NM cables.
 