Thoughts on this one?
Can't wait to see the difference of opinion on this
Can't wait to see the difference of opinion on this
Jim W in Tampa said:They do not require staples and actually the fewer staples the better.
ivsenroute said:Panel location was in the garage
mdshunk said:I'm not sure where the dividing line is, but I'd guess off the cuff that you can run about 12 or 15 #12 home runs for the price of 200 amp SER. I never really sat down to figure it out.
ivsenroute said:Thoughts on this one?
Can't wait to see the difference of opinion on this![]()
Like pulling teeth in most Resi applications to get a panel near where it SHOULD be - even getting creative about it can add costs or complication thet the commitee frowns on. what is needed is better looking equipment that is invisable.iwire said:Seems to me the panel was not located where it could do the most good.
iwire said:I assumed that, but would it not have been more cost effective to install a meter main and move the panel closer to the loads it serves?
Just thinking out load here. :smile:
I never really did single family homes but I have done a lot of condos and apartments, we install the panel in or close to the kitchen to keep the branch circuits short. :smile:
Jim W in Tampa said:Before the high copper prices the normal install is back to back service in garage.
In this instance, I agree.ivsenroute said:Looking beyond a "bundling" concern which is not as significant of an issue to me
Yes, it is covered - assuming it is accessible, it is an accessible attic space. The ceiling trusses are the "floor joists" of the attic space.Call it a technicality but this situation is not really covered so we must look at the intention of the code.
320.23(A) ...Where this space is not accessible by permanent stairs or ladders, protection shall only be required within 1.8 m (6 ft) of the nearest edge of the scuttle hole or attic entrance.
Why would the number of cables matter in regards to physical protection?Stapling would still be required at appropriate intervals but the 2x4 strip used as a guard strip is questionable since there are so many cable run together.
Yes, it would pass, and yes, I have done it.Would this pass in your jurisdiction? Has anyone ever has a situation like this and what would the alternative be for a setup like this with the main panel being in the garage.