Burial Depth for Concrete Encased PVC with traffic

Status
Not open for further replies.

adalewhite

Master Electrician, Electrical Design, Veteran
Location
Georgia
Occupation
Licensed Electrician, Electrical Designer, A&E PM
We have a concrete encased PVC duct with 480V which will pass under a drive.

Table 300-5 calls for 24" minimum cover in Column 3 for nonmettalic raceway under driveways, parking lots etc. I've asked several engineers if there is a reduced depth allowed since we are encasing in concrete and none can come to a clear rule for below 600V.

Table 300-50 Minimum Cover Requirements for above 600V Exception No.2 seems to allow the reduction of cover 6" for every 2" of concrete protection.

What burial depth requirement would be correct for 480V feeders in concrete encased PVC under a drive or parking lot?

We've got a trech open waiting on conduit and an interpretation :eek:
 

gwz2

Senior Member
Location
Indiana
Re: Burial Depth for Concrete Encased PVC with traffic

See 1986 TCR proposal 3-30 on page 204 and 1992 TCR proposal 3-54 on page 193.

The CMP indicates 24" of cover even if in 24" of concrete.
 