Confused…
Given: 20 A branch circuit to shed 75’ away.
Tapped from the load side of a gfci receptacle on the side of the house.
Thwn conductors in pvc conduit.
I contend since conductors are gfci protected it can be buried at 12” using 300.5 column 4.
Was told since in conduit I have to use column 3, so 18” depth.
Seems there is already additional protection to the 12” guideline, why do I need the added depth?