Burial depth on pathway with issues

Status
Not open for further replies.
Location
Midwest
Occupation
Electrical Engineer - Power and Controls
Have a dirt pathway on site between two ponds,
looking to run a duct bank under the dirt pathway. per nec i see that roadways indicate a minimum of 24" burial depth. is this a roadway?. is a pathway that sees vehicles/telehandlers need burial of cable to to be at 24 minimum depth? does concrete encasement reduce this burial depth any? code reference? The area of this pathway between two ponds could cause roadway stability issues during/after excavation as is why i have concern about this.

thanks in advance.
 
Last edited:

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Underground cables and conduits.
 

Attachments

  • NEC - Underground Cables & Conduits.pdf
    42.1 KB · Views: 4

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Dig an access trench on either side of the path / roadway to the desired depth ... take a rigid stick of conduit with a hose adapter and push it through.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Have a dirt pathway on site between two ponds,
looking to run a duct bank under the dirt pathway. per nec i see that roadways indicate a minimum of 24" burial depth. is this a roadway?. is a pathway that sees vehicles/telehandlers need burial of cable to to be at 24 minimum depth? does concrete encasement reduce this burial depth any? code reference? The area of this pathway between two ponds could cause roadway stability issues during/after excavation as is why i have concern about this.

thanks in advance.
Did you look at table 300.5?
 