Hello, Everyone...
We are installing an outdoor hydrogen refueling system (for the forklift fleet) at an automobile plant. Our conduit is sch. 40 PVC with RGC risers for the stub-up locations. We have typically relied upon Table 300.5 to determine our burial depth for these facilities. One of the project managers (naturally) questioned the burial depth, stating that 514.8 should be considered for the installation because the location was Class 1 (Divisions 1 & 2). My argument was that because the entire location is under a 6" concrete slab outside a building, that 300.5 applied. What say you?
We are installing an outdoor hydrogen refueling system (for the forklift fleet) at an automobile plant. Our conduit is sch. 40 PVC with RGC risers for the stub-up locations. We have typically relied upon Table 300.5 to determine our burial depth for these facilities. One of the project managers (naturally) questioned the burial depth, stating that 514.8 should be considered for the installation because the location was Class 1 (Divisions 1 & 2). My argument was that because the entire location is under a 6" concrete slab outside a building, that 300.5 applied. What say you?