Burial depth

Status
Not open for further replies.

nizak

Senior Member
Is there a minimum depth requirement for a #4 Cu GEC run between 2 ground rods?

AHJ is saying 12” but didn’t give a code reference on the inspection report.
Thanks
 
This was new in the 2017 code.
250.64(B)(4) In Contact with the Earth.
Grounding electrode conductors and grounding electrode bonding jumpers in contact with the earth shall not be required to comply with 300.5, but shall be buried or otherwise protected if subject to physical damage.
 