burial depth

Status
Not open for further replies.
Location
Spokane Washington
Occupation
electrician
Is there anything that covers conduit burial depth under a load bearing foundation or is this covered in table 300.05 ? I cant find anything else, I have engineers asking if PVC is ok at 4" below a 10" concrete slab that is a structural foundation. no vehicular traffic on the slab.
 
Nothing in the NEC regarding conduit below load bearing portions of a structure. The structural engineer should decide if the PVC is okay in that location.
 