We Are Installing Conduit At A New Gas Station
Our Conduit Is Under 6" Of Concrete
The Inspector Rejected Our Installation Due To Depth Of Conduits
He Quoted 300.5 And Tells Me That The Conduits Must Be 24".
My Interpetation Of This Code Is That Under 2" Of Concrete That The Depth Only Needs To Be 6". We Are At An Impass And I Need Some Back Up.
Thank You
Greg
THANKS FOR THE REPLY
I WOULD THINK THAT THE 24" UNDER ROAD WAYS WAS DUE TO THE SURFACE BEING ASPHALT THE CODE DOES NOT SPECIFY CONCRETE OR ASPHALT
Our Conduit Is Under 6" Of Concrete
The Inspector Rejected Our Installation Due To Depth Of Conduits
He Quoted 300.5 And Tells Me That The Conduits Must Be 24".
My Interpetation Of This Code Is That Under 2" Of Concrete That The Depth Only Needs To Be 6". We Are At An Impass And I Need Some Back Up.
Thank You
Greg
THANKS FOR THE REPLY
I WOULD THINK THAT THE 24" UNDER ROAD WAYS WAS DUE TO THE SURFACE BEING ASPHALT THE CODE DOES NOT SPECIFY CONCRETE OR ASPHALT