Whats your take on conduits under 6'' of concrete (pvc and rigid) in a machine shed, would you view them as being under a building, or consider the interior as a driveway?
Around here 4" of concrete is what driveways are, so with your 6" I would say that you are outside the building. Local rules may vary so consult your AHJ
Machine shed floor is 6'' of concrete, I want to ground rough conduits from panel to various locations, just debating whether i need to go deeper the just scratching conduits into gravel base before pour.
Machine shed floor is 6'' of concrete, I want to ground rough conduits from panel to various locations, just debating whether i need to go deeper the just scratching conduits into gravel base before pour.
I'd say you're definitely under a building. In the past I've always used pvc in this situation and just scratched it in under finished grade enough to protect it until the concrete was poured. Might wanna keep an eye on it while the concrete contractors are working to make sure they don't damage it and maybe run a fish tape through it before they pour.