Hello All,

Two questions.

First, I will like some clarification on the statement" Emerging from grade" mentioned in page 302 of the 2011 NEC.

Second, I will like members professional thoughts on installing a direct buried cable below a concrete water ditch. Does this violates the code? Cna you help me finding some support information on reasons why not to do this?

Thanks in advance.
 
Hello All,

Two questions.

First, I will like some clarification on the statement" Emerging from grade" mentioned in page 302 of the 2011 NEC.

Second, I will like members professional thoughts on installing a direct buried cable below a concrete water ditch. Does this violates the code? Cna you help me finding some support information on reasons why not to do this?

Thanks in advance.

The only place I can find this phrase is in 300.1(D). I think it means you have to protect DB cables to the specified distance below grade. i don't see what else it could mean.

Off the top of my head I can't see any reason the code would prohibit running a cable under a ditch as long as the minimum cover requirements were met and the cable was suitable for direct burial. I might argue it would be a bad idea if it was a dirt ditch as erosion might over time reduce the cover that is required, but that would not likely be an issue with a concrete ditch.
 