In my previous post about wire pull problems, I was surprised to learn that several members replied that they would not swab buried conduits as a matter of practice, unless it was specifically stipulated in their contract. The reason I was surprised is because, at ~$100, a swab is not that expensive for a contractor bidding on large commercial jobs, and it doesn't really add any time to the job: the swab can be pulled through the conduit as the mule tape is pulling in the pull rope.
Whether or not it was stipulated in the contract, if I were the electrical contractor on our particular installation, I would have wanted to swab for no other reason than to make the pull easier, let alone minimize the risk of damage to the insulation and future warranty service. I think these images will show why...
The following illustration shows the relation between the distribution panel, the Christy box, and the conduits. The relative elevations in the diagram are correct, but the slope of the conduits is exaggerated because the actual distance between panel and box is 185 feet. It's important to note, however, that the conduits do slope downhill from the box to a low-point below the panel.
The Christy box was buried in the base of an earthen levee; outside the levee is a saltwater creek. Because our property is below sea level at high tide, we have a high ground-water table and intrusion of salt water into our soil. After fifteen years, ground water ingress had washed 12 inches of soil into the Christy box, depositing it in the bottom of the box and completely covering the conduit openings.
Christy box uncovered (some inside soil already dug away to expose top of conduit):
Detail inside Christy box:
After soil was removed:
Common sense dictates that at least some soil would have been washed into the downward sloping conduits. In the next photo, you can still see soil inside the openings of the conduits, even after cleaning out by hand.
Detail of conduit openings and feeders to distribution panel:
If you were the contractor on this job and you saw this, would you swab the conduits even if your contract didn't require it?
Whether or not it was stipulated in the contract, if I were the electrical contractor on our particular installation, I would have wanted to swab for no other reason than to make the pull easier, let alone minimize the risk of damage to the insulation and future warranty service. I think these images will show why...
The following illustration shows the relation between the distribution panel, the Christy box, and the conduits. The relative elevations in the diagram are correct, but the slope of the conduits is exaggerated because the actual distance between panel and box is 185 feet. It's important to note, however, that the conduits do slope downhill from the box to a low-point below the panel.
The Christy box was buried in the base of an earthen levee; outside the levee is a saltwater creek. Because our property is below sea level at high tide, we have a high ground-water table and intrusion of salt water into our soil. After fifteen years, ground water ingress had washed 12 inches of soil into the Christy box, depositing it in the bottom of the box and completely covering the conduit openings.
Christy box uncovered (some inside soil already dug away to expose top of conduit):
Detail inside Christy box:
After soil was removed:
Common sense dictates that at least some soil would have been washed into the downward sloping conduits. In the next photo, you can still see soil inside the openings of the conduits, even after cleaning out by hand.
Detail of conduit openings and feeders to distribution panel:
If you were the contractor on this job and you saw this, would you swab the conduits even if your contract didn't require it?