EPRI did a research project to provide an initial evaluation of the impact of concrete blocks on substation safety and performance as well as recommendations for dealing with this issue. The study produced a number of important and useful recommendations.
A secondary objective is to bring these issues to the attention of industry groups involved with standards development, such as the Institute of Electrical and Electronics Engineers (IEEE) for possible incorporation into the standards as it is written in the article.
Results & Findings
The study showed that the presence of concrete blocks in the vicinity of a substation might generate increased touch and step voltages, especially in cases where concrete blocks are outside
the substation fence but close to it and are not bonded to the substation grounding system.
However, in cases where the concrete blocks are bonded to the substation grounding system, the effect was beneficial in most cases considered in this parametric study. In any case, only a small amount of fault current usually goes through the steel rebar. The performed parametric study was limited in scope and therefore does not capture all possibilities that may occur. For example, the study has not addressed the issue of lightning currents and what percentage of lightning current may flow in steel rebar bonded to the grounding system.
See:
EPRI
Effects of Steel Reinforced Concrete on
Grounding System Performance