Question about table 300.5
In column 4 it states that residential branch circuits rated at 120 volts or less with GFCI protection and a maximum overcurrent protection of 20 amps or less. In the 1st location specified it says it has to be 12” deep. My question is that it doesn’t Specify if it is 120 V to ground or Has to be an exact 120 V circuit. If I am feeding just a pool pump that is 240v which is 120v to ground. It is just a branch circuit and not a feeder so it will be GFCI protected from the main panel. Every other County I work in interprets it to be 120v to ground. I had an inspector in another County fail me saying that it is only 120v period. My thoughts are if you had 2 or 3 circuits in a conduit and they were all 120v circuits, you would still get 240v line to line if someone hit it with a shovel. He told me that if all 3,5 or how ever many circuits I have in the conduit are all 120v then I would be fine. But it’s the exact same thing, you are going to get 120v to ground and 240v line to line from any of the circuits that are on separate phases. So how is that any different? How is this supposed to be interpreted?
In column 4 it states that residential branch circuits rated at 120 volts or less with GFCI protection and a maximum overcurrent protection of 20 amps or less. In the 1st location specified it says it has to be 12” deep. My question is that it doesn’t Specify if it is 120 V to ground or Has to be an exact 120 V circuit. If I am feeding just a pool pump that is 240v which is 120v to ground. It is just a branch circuit and not a feeder so it will be GFCI protected from the main panel. Every other County I work in interprets it to be 120v to ground. I had an inspector in another County fail me saying that it is only 120v period. My thoughts are if you had 2 or 3 circuits in a conduit and they were all 120v circuits, you would still get 240v line to line if someone hit it with a shovel. He told me that if all 3,5 or how ever many circuits I have in the conduit are all 120v then I would be fine. But it’s the exact same thing, you are going to get 120v to ground and 240v line to line from any of the circuits that are on separate phases. So how is that any different? How is this supposed to be interpreted?