I recently wired 2 3phase motors of 2HP and 10HP for a spray booth in a paint shop. The 10HP motor is for the air compressor and is 208-230/460Volt 30-28/14Amp, and is fed from a 3phase 40 Amp Mag starter from a 3phase 40Ampfused disconnect, which in turn is fed by a 40Amp 3pole breaker in a 240 Volt 3phase; 3 wire; delta panel. Leg A and C measure 120 Volts to ground, Leg B measures 208 Volts to ground, and 240 Volts phase to phase. The Compressor is wired for Low Voltage Delta I joined wires A-1-7-6, B-2-4-8, C-3-5-9. The mag starter coil is activated by a pressure switch on the compressor. The T-wires in the pecker head of the 10Hp motor on the compressor were black and lightly burned when I had made the connections. I inserted the wires through heat shrink, and relabeled them after half an hour of the process of elimination and troubleshooting with the knowledge that the previous shop was a 240Y 3W system. The 3pole 40amp breaker at the panel trips after the compressor runs for 10 seconds. I checked the rotation of the fan on the compressor and everything checks out. What else can I do to get this motor running and is there a possibility that the windings are going to smoke out?
Now the 2HP motor is a fan motor installed for the spray booth, and it is 3phase 230/460Volt 6.2/3.1Amp. It is fed from a 15Amp fused disconnect, which in turn is fed from a 20amp fused 3p CB. I also wired this motor for low voltage delta. I ran the motor for 10 seconds the check rotation. I did this a couple more times for the owner of the paint shop. The next morning I received a rather devastating call that the fan motor smoked out, and needed to be replaced with the money from my pocket. Both motors were previously wired for Low Voltage Wye because the previous shop had 240V 3W Wye available power. I've checked all my connections and nothing has turned out to be wrong what can I do? Now I have to call an industrial service electrician for a second opinion just to prove to the customer that the motor burned out through no fault of my own. I've attached pictures of my work. Please help me I don't know what I could have done wrong.