Heres what I know.
480V/3ph/60Hz delta power system
The 480V loads in this sytem are as follows: 2 - small (<3HP) motors, 2 - 20KW immersion heaters.
This control panel has 70A Bussmann class J fuses in its main disconnect, 30A littelfuse ccmr-30 fuses in its branch circuit before the heater contactors.
I'm sent a picture of a control panel with the one heater fuse block completely charred, damaging wires throughout the panel. L2 fuse was history (exploded), L1 and L3 fuses damaged. The other heater fuse block blew L2 as well but had no charring. Two phases in the main disconnect (70A), L2 and L3, were open.
The service technician onsite indicated that the fuses in the second heater block were hot to the touch as well.
What could have caused this to happen? All the wiring downstream from the charred fuseblock appears to have its insulation. Why would these fuses not have just opened? And why would the main disconnect fuses upstream open?
I will get you more info as soon as I can get it. Any light you can shed on this would be greatly appreciated.
Thanks in advance. :shock: I've had this expression on my face all day.
480V/3ph/60Hz delta power system
The 480V loads in this sytem are as follows: 2 - small (<3HP) motors, 2 - 20KW immersion heaters.
This control panel has 70A Bussmann class J fuses in its main disconnect, 30A littelfuse ccmr-30 fuses in its branch circuit before the heater contactors.
I'm sent a picture of a control panel with the one heater fuse block completely charred, damaging wires throughout the panel. L2 fuse was history (exploded), L1 and L3 fuses damaged. The other heater fuse block blew L2 as well but had no charring. Two phases in the main disconnect (70A), L2 and L3, were open.
The service technician onsite indicated that the fuses in the second heater block were hot to the touch as well.
What could have caused this to happen? All the wiring downstream from the charred fuseblock appears to have its insulation. Why would these fuses not have just opened? And why would the main disconnect fuses upstream open?
I will get you more info as soon as I can get it. Any light you can shed on this would be greatly appreciated.
Thanks in advance. :shock: I've had this expression on my face all day.