Interesting problem.
Why did the fuses burn out on the following system?
SYSTEM SPECS:
Built in 2014.
4 strings of Solar World 270W modules. (8.81A Imp and 9.44A Isc)
All 4 strings pass through a Soladeck J-box mounted to roof surface.
8 fuses inside Soladeck: 4 + and 4 - fuses.
20A fuses.
Strings just pass through fuses to inverters - no combining in Soladeck. (All PV source circuit conductors continue individually to inverters.)
2 strings feed one inverter and 2 feed the other.
2 @ SMA SB5000TL-US-22, 5,000 W inverters.
Dual input/MPPT inverter.
Ungrounded system.
ISSUE:
Found 2 fuses burned out. Probably over the last year, one fuse in string #2 and one in string #3 burned out.
These feed separate inverters.
Insides of most white plastic fuse-holders browned and several fuseholders fused/melted together.
Wire ends near terminals of fuse-holders blackened.
Fuseholders browned even where fuse was intact, but to slightly lesser degree than the fuse-holders that had failed fuses inside.
Both inverters working fine on one remaining string each when I visited. Green lite solid.
--------------------------------------------------------------------
I have 4 questions and I will try not lead in any direction.
1. Why would 20A fuses burn out on a roughly 9 Amp circuit?
2. Was fusing even required per NEC on this system? (No combining of strings and separate inverters also. But 4 pv source circuits do share same conduit to inverter area.)
3. Regardless of NEC, does fusing serve any safety purpose in such a case?
4. Would you replace fuses with 20A, 25A, 30A, "slugs" (dummy "fuse", solid metal, not a fuse), or....?
Why did the fuses burn out on the following system?
SYSTEM SPECS:
Built in 2014.
4 strings of Solar World 270W modules. (8.81A Imp and 9.44A Isc)
All 4 strings pass through a Soladeck J-box mounted to roof surface.
8 fuses inside Soladeck: 4 + and 4 - fuses.
20A fuses.
Strings just pass through fuses to inverters - no combining in Soladeck. (All PV source circuit conductors continue individually to inverters.)
2 strings feed one inverter and 2 feed the other.
2 @ SMA SB5000TL-US-22, 5,000 W inverters.
Dual input/MPPT inverter.
Ungrounded system.
ISSUE:
Found 2 fuses burned out. Probably over the last year, one fuse in string #2 and one in string #3 burned out.
These feed separate inverters.
Insides of most white plastic fuse-holders browned and several fuseholders fused/melted together.
Wire ends near terminals of fuse-holders blackened.
Fuseholders browned even where fuse was intact, but to slightly lesser degree than the fuse-holders that had failed fuses inside.
Both inverters working fine on one remaining string each when I visited. Green lite solid.
--------------------------------------------------------------------
I have 4 questions and I will try not lead in any direction.
1. Why would 20A fuses burn out on a roughly 9 Amp circuit?
2. Was fusing even required per NEC on this system? (No combining of strings and separate inverters also. But 4 pv source circuits do share same conduit to inverter area.)
3. Regardless of NEC, does fusing serve any safety purpose in such a case?
4. Would you replace fuses with 20A, 25A, 30A, "slugs" (dummy "fuse", solid metal, not a fuse), or....?