Loose hot leg connection or fault to ground.Why only one side? Loose?
The terminations on the device seemed good. I guess it would have to be the cord end or as someone else said the inside contacts.Chicken or the egg?
Was it the cord end plugged into it that caused the issue or was it the loose screw on the device?
YupSpringy metal weakens with heat, which loosens contact, which causes more heat, and it snowbsalls over time.
If the voltage drop is concentrated in the outlet due to a resistive connection, resistance = heat, so yes. If the Vd is in the wiring, then the heat would be distributed over the length of the wire, so probably not.Might sound crazy, but consider checking voltage drop. Saw something similar and after some investigating the electrician tested the voltage drop under load and it was extreme. I don't remember exactly but I think it was a 30-40% drop when under load, he used a hair dryer. I think ultimately it was a POCO issue.
Someone with way more knowledge than me can verify this might be the problem, or politely explain to me why I ain't got a clue. Thanks in advance for any education, always ready to learn more.
I zoomed in on the yoke. Spec grade Hubbell.Can you post a picture of the back? Looks like a $.50 Menards outlet.
Well aren't you the smart one! LOL....Hubbell is generally top grade stuff. I don't see much of their stuff going bad.I zoomed in on the yoke. Spec grade Hubbell.
Been there. Was it NW of Pleasanton?one of the stranger problems I came across was, an inside cat that was peeing into a wall receptacle behind a sofa. Aside from the smell, it shorted killed power in two rooms.
The cat was lucky that it was not grounded.one of the stranger problems I came across was, an inside cat that was peeing into a wall receptacle behind a sofa. Aside from the smell, it shorted killed power in two rooms.