Burnt Ballasts

Status
Not open for further replies.

solis

Member
Recently found I eight light fixtures 2 per pole all ballasts were burnt to a crisp. The Breaker was tripped, but after disconnecting all the lights, it reset. No evidence of lightening, the customer asked why this happened. I said I would ask if anyone knew.
Any idea's?
 

Attachments

  • 0618151131.jpg
    0618151131.jpg
    150.8 KB · Views: 0

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Recently found I eight light fixtures 2 per pole all ballasts were burnt to a crisp. The Breaker was tripped, but after disconnecting all the lights, it reset. No evidence of lightening, the customer asked why this happened. I said I would ask if anyone knew.
Any idea's?

That will trip a breaker and give you heart burn!:D
 

kwired

Electron manager
Location
NE Nebraska
The thing that doesn't make sense is how they all fail at same time unless it is improper voltage/connected to wrong voltage tap or a lightning event. Lightning probably would see other items effected as well, unless these lights is about all there is to have any damages.

Wrong voltage tap will show up fast if you mess up with 120 vs other taps, but using the wrong 208, 240 or 277 taps could result in the thing working but will take some time to burn out. Supply the unit with nominal 208 but is running near 215 - and it may run a very long time if connected to the 240 tap, supply it with nominal 240 but is running near 250 - it may run a long time if connected to the 277 tap - many of these units are set up for 277 as shipped - maybe the installer didn't pay close enough attention to what tap was used?
 

electricalist

Senior Member
Location
dallas tx
Sorry I hadnt looked that close.
I have seen quite a few that the whole thing had blown out, but I dont know if they were from bad ballast.
Someone stole the #8 s from pole to pole.

Sent from my SPH-D710BST using Tapatalk
 

Electric-Light

Senior Member
Sorry I hadnt looked that close.
I have seen quite a few that the whole thing had blown out, but I dont know if they were from bad ballast.
Someone stole the #8 s from pole to pole.

Sent from my SPH-D710BST using Tapatalk
The arc tube is glowing orange hot if you ever look at it shortly after the power is turned off. Excess current means excess power... it gets even hotter and glass will eventually rupture.

Traditional ballasts are very durable. Unlike electronic LED ballasts, they only fail if they get hot enough to char the insulation or gets enough over-voltage to flash over. To lose that many ballasts all at once has to be incorrect voltage, wiring or ballast/lamp/cap combo.
 