sethas
Member
- Location
- Los Banos, CA.
I went to service call at a mobile home park on friday. The customer said that the ground wire, the one bonded to the water main, had become extremely hot to the touch, so hot in fact that it caught a motorcycle cover on fire. An electrician had been called out before me, and had cleaned off the corrosion around the connection, and then proceeded to re-tighten the connection. He then informed her that she needed a new pedestal. The pedestal is a 30A 120V unit. It has an illeagal tap off of it that controls two 15A 120V circuits, with a shared neutral. At the main disconect, the hot conductor and the neutral conductor are the only present wires for the pedestal, no ground to be found. At the mobile home, or rather a poorley converted RV, the panel, on the RV, appears to bonded correctly to the frame. At the pedestal, there are three wires, a hot conductor, a neutral conductor, and a ground wire, which is bonded to the water main. I presently get 120V from the hot to neutral, and from the hot to ground. There is no continuity from the ground to the hot or the neutral, and no voltage from the neutral to the ground. I suspect that the ground wire travels only from the water main, to the pedestal, approx. 2 feet. Any ideas why it would get so hot as to catch fire? What is going on, and why? Thanks for any input.