I need to move a service panel that has a number of raceways coming in the bottom. The slab has been cut out of the building and conduits exposed.
One way to do this would be to carefully cut each pipe where is enters the building(under the footing), pull the pipe off the existing wire, install C type conduit bodies, re-pipe everything to new location, pull wire back in through the C, done.
I am trying to avoid pulling all the wire entirely from the pipes due to length of the runs/not knowing how easy it would be to get back in.
The question is can I then make the C fittings non-accessible by embedding them in concrete? There would be no junctions and theoretically they could be fished through in the future seeing as they're straight. I know it's not ideal but sometimes compromises have to be made.
Thanks in advance.