Bus bars traversing over bus bars

Status
Not open for further replies.

mbrooke

Batteries Included
Location
United States
Occupation
Technician
When crews service a bus bar, how far must de-enerigzed bars from energized bars? Can bus bar insulators be replaced live and how often do they fail prior to 40 in-service years?

The design to the right is economical to build, but repair down the road is being called into question.





1e25c85101d0730449ac52b45bc9b9ad.jpg
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
In my opinion, what do you need are bus disconnectors. So you could de-energize a system and work on another.
If it is height enough you may pass the connection bar under the main busbar. Double Busbar Connections.jpg
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
In my opinion, what do you need are bus disconnectors. So you could de-energize a system and work on another.
If it is height enough you may pass the connection bar under the main busbar. View attachment 16768

What are those? :dunce:

I know of pentographs being used at 132 and 400kv but don't know of any made for 34.5kv. Unless you are thinking of something else.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
I am sorry. At first I didn’t know the voltage. Second neither even for above 132 kV indoor distribution like this I did not see for a long time. Now GIS it is more convenient. By the way, the line of circuit breakers are the ancient “Bulk Oil Circuit Breakers", indeed? I saw one like this for the last time 50 years ago.
For up to 36 kV I don’t know open installation else but Switchgear –metal clad-only.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
I am sorry. At first I didn’t know the voltage. Second neither even for above 132 kV indoor distribution like this I did not see for a long time.

This is an outdoor substation.

Now GIS it is more convenient. By the way, the line of circuit breakers are the ancient “Bulk Oil Circuit Breakers", indeed? I saw one like this for the last time 50 years ago.


Vacuum breaker:


http://www.abb.com/product/db0003db004279/c12573990063647085256aea006dbae3.aspx

http://inv.bassmachinery.com/q/nlist/=,000920,20275734

Although they do look like bulk oil breakers lol. FWIW the final design might have SF6 instead.

For up to 36 kV I don’t know open installation else but Switchgear –metal clad-only.


Its ok, it varies. :)
 