Bus Duct Ampacity

Status
Not open for further replies.

PhaseShift

Senior Member
When using bus duct what table do you use for the ampacity of the bus duct? Do you use 310.16? Can you use the 90deg C column or must you use the 75deg column still?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
It is not in the NEC tables. You tell the manufacturer what ampacity you need, and they sell it to you.
 

Smart $

Esteemed Member
Location
Ohio
When using bus duct what table do you use for the ampacity of the bus duct? Do you use 310.16? Can you use the 90deg C column or must you use the 75deg column still?
The only ampacity requirement for busbar in the NEC that I'm aware of is in 366.23.
366.23 Ampacity of Conductors.

(A) Sheet Metal Auxiliary Gutters.
Where the number of
current-carrying conductors contained in the sheet metal auxiliary
gutter is 30 or less, the adjustment factors specified in
310.15(B)(3)(a) shall not apply. The current carried continuously
in bare copper bars in sheet metal auxiliary gutters shall
not exceed 1.55 amperes/mm? (1000 amperes/in.?) of cross
section of the conductor. For aluminum bars, the current carried
continuously shall not exceed 1.09 amperes/mm? (700 amperes/in.?)
of cross section of the conductor.

 