I have a situation where bus duct was installed vertically leaving a switchboard with a 90? section and traveling over the front of the switchboard. The SB is about 5' high and the underside of the bus duct is 6'2". Seems like the required 6'6" has to be met once the bus duct extends beyond 6" past the front face of the switchboard. Any opinions?