mayanees
Senior Member
- Location
- Westminster, MD
- Occupation
- Electrical Engineer and Master Electrician
I have a situation where I've measured transient voltages upon energization of a 700' section of 480V bus duct.
The busduct feeds a Data Center. Transients have blown filter capacitors, so the filter was removed and the line was energized while it still had a 150 kVa transformer and a 125 kVA system connected. Voltages were measured as high as 2100 Volts. I thought perhaps ferroresonance for this.
But when the loads were removed and the bus was energized, a 1900 Volt, 2ms spike was detected. My thoughts got the 540' section of Eaton Pow-R-Way III sandwich bus and the two (2) 150', 1000-amp busduct sections off of it.
Comments welcomed.
John M
The busduct feeds a Data Center. Transients have blown filter capacitors, so the filter was removed and the line was energized while it still had a 150 kVa transformer and a 125 kVA system connected. Voltages were measured as high as 2100 Volts. I thought perhaps ferroresonance for this.
But when the loads were removed and the bus was energized, a 1900 Volt, 2ms spike was detected. My thoughts got the 540' section of Eaton Pow-R-Way III sandwich bus and the two (2) 150', 1000-amp busduct sections off of it.
Comments welcomed.
John M