How would you guys feed a 480 volt piece of equipment with say 20fla and a 30 amp main. Would you feed it with #10 and 30 amp fuses in the bus duct or would you up the fuse size and size the feed conductors accordingly?
I guess I'm missing the big picture. Why a breaker and a fuse?
In general 240.4(D) would dictate that your 10's are fed with a 30A breaker.
Volta you are correct. Is there any reason that would prevent you from upsizing the fuses if the feed conductors are sized properly as well?