I'm looking at short circuit ratings for 480V (635V Max) Non-Seg Bus Duct with the following ratings:
2-second Withstand: 63kA
1-second Withstand: 89kA
Momentary Peak: 170kA
Momentary Asymmetrical: 100.8kA
When comparing these ratings to the calculated available LV fault duty do you use the 2-second rating or the 1-second rating. For a particular location the available short circuit current is calculated at 6700A. If this is to be compared to the 2-second rating than this Bus Duct would be overdutied?
The 2-second rating listed above is the maximum rating available for this Bus Duct. Has anyone run across a similar case with BusDuct being overdutied?
Why does the LV Bus duct have a momentary rating associated with it? I have always though that this momentary rating was reserved for MV equipment which has both interrupting and momentary ratings and that LV equipment only has an interrupting or withstand rating?
2-second Withstand: 63kA
1-second Withstand: 89kA
Momentary Peak: 170kA
Momentary Asymmetrical: 100.8kA
When comparing these ratings to the calculated available LV fault duty do you use the 2-second rating or the 1-second rating. For a particular location the available short circuit current is calculated at 6700A. If this is to be compared to the 2-second rating than this Bus Duct would be overdutied?
The 2-second rating listed above is the maximum rating available for this Bus Duct. Has anyone run across a similar case with BusDuct being overdutied?
Why does the LV Bus duct have a momentary rating associated with it? I have always though that this momentary rating was reserved for MV equipment which has both interrupting and momentary ratings and that LV equipment only has an interrupting or withstand rating?