Bus Duct Voltage Drop

Status
Not open for further replies.

Turk1957

Member
Been given many different answers on this one, so I figured I would come back to the folks I trust the most... 200,000 square foot addition to an assembly facility.... Thinking of extending an existing 1600A. plug-in bus duct into the new area, but not certain of my limitaions in regard to voltage drop... Any suggestions? Thanks in advance for any help...
 
Been given many different answers on this one, so I figured I would come back to the folks I trust the most... 200,000 square foot addition to an assembly facility.... Thinking of extending an existing 1600A. plug-in bus duct into the new area, but not certain of my limitaions in regard to voltage drop... Any suggestions? Thanks in advance for any help...

I can't even fathom what kind of answer do you expect without supplying and load and length data. Lay it out, pinpoint your load take-offs, play with diversity and the manufacturer will give you the exact data you need.

You voltage drop is not expected to exceed 2% through your network - bus - and an additional 3% for the branch drops.
 
Last edited: