Bus Duct

Status
Not open for further replies.

azap

Member
Article 368 is unclear to me. Can a busduct that is non-ventilated be above an acustical ceiling? There are no additional breakers at the point where we want to drop the ceiling below it. Is this legal? Thank you
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Re: Bus Duct

I believe any totally enclosed busway is allowed above ceilings that are not air-handling spaces. However, 368.10(B)(2) prohibits plug-in style busway in environmental air spaces.
 