I am having an OCD moment with visual design on one of my circuits.
3 Pole ABB OS Switch Fuse Disconnector. 125A a pole.
I either bolt all 3 connection lugs on the bottom of the fuse switch disconnector straight across the positive busbar and feed out the top with cable to each invertor.
or
Run 50mm cable from the busbar to each lug on the Switch fuse disconnector and the same out the top. (This will look nicer but bother me about the run between the busbar and the fuse which will be satisfied by Adiabatic calcs for 50mm and 12kA for 0.2secs) but still always bothers me as I like to bolt the fuse bases to the busbars. The busbar will be protected by a 500A fuse.
I just want it to look nice and don't really want a busbar hanging off my switch fuse disconnector.
Opinions please.
3 Pole ABB OS Switch Fuse Disconnector. 125A a pole.
I either bolt all 3 connection lugs on the bottom of the fuse switch disconnector straight across the positive busbar and feed out the top with cable to each invertor.
or
Run 50mm cable from the busbar to each lug on the Switch fuse disconnector and the same out the top. (This will look nicer but bother me about the run between the busbar and the fuse which will be satisfied by Adiabatic calcs for 50mm and 12kA for 0.2secs) but still always bothers me as I like to bolt the fuse bases to the busbars. The busbar will be protected by a 500A fuse.