I have a 1200A, 3 phase, 3W bus with the following breakers in the SLD; 100A, 100A, 75A, 50A, 100A, 100A. In addition, there is a 200A ATS, 300A Meter, 300A Generator. The new addition would be a 200A breaker. According to 705.12(b), I would need to upsize the busbar. The EE states that is incorrect, but will not explain how that is possible. Can someone explain?