352.46 Bushings.
Where a conduit enters a box, fitting, or other enclosure, a bushing or adapter shall be provided to protect the wire from abrasion unless the box, fitting, or enclosure design provides equivalent protection.
FPN: See 300.4(G) for the protection of conductors 4 AWG and larger at bushings.
IMO, you need a bushing. 352.46
IMO, you need a bushing. 352.46. If you use a slip fitting adapter then I say no you don't.