Why? Because it says rigid conduit? The engineer will say it does pertain to EMT regardless of what NEC definition is. He'll say rigid conduit is intended to mean non flexible conduit.It doesn't pertain to EMT and other connectors.
Well they used the incorrect terminology so they're wrong. EMT is not even conduit it tubing.Why? Because it says rigid conduit? The engineer will say it does pertain to EMT regardless of what NEC definition is. He'll say rigid conduit is intended to mean non flexible conduit.
It is technically Rigid Metal Conduit and not Rigid conduit so engineer may have case.
I have never seen specs that have a different category for EMT. It is always under the section for conduit. I would say that this engineer will require it on all types of "rigid conduit". But this is when an RFI should be sent for clarification.Well they used the incorrect terminology so they're wrong. EMT is not even conduit it tubing.
well...240.4(A)(2) would require that locknut to be bonded if the enclosure is nonmetallicI inspected a job yesterday where they had bonding bushings on 16 conduits,,,,,, all PVC. the only thing getting bonded was the locknut.