Bushing

It doesn't pertain to EMT and other connectors.
Why? Because it says rigid conduit? The engineer will say it does pertain to EMT regardless of what NEC definition is. He'll say rigid conduit is intended to mean non flexible conduit.

It is technically Rigid Metal Conduit and not Rigid conduit so engineer may have case.
 
Why? Because it says rigid conduit? The engineer will say it does pertain to EMT regardless of what NEC definition is. He'll say rigid conduit is intended to mean non flexible conduit.

It is technically Rigid Metal Conduit and not Rigid conduit so engineer may have case.
Well they used the incorrect terminology so they're wrong. EMT is not even conduit it tubing.
 
Well they used the incorrect terminology so they're wrong. EMT is not even conduit it tubing.
I have never seen specs that have a different category for EMT. It is always under the section for conduit. I would say that this engineer will require it on all types of "rigid conduit". But this is when an RFI should be sent for clarification.
 
I inspected a job yesterday where they had bonding bushings on 16 conduits,,,,,, all PVC. the only thing getting bonded was the locknut.
 
I inspected a job yesterday where they had bonding bushings on 16 conduits,,,,,, all PVC. the only thing getting bonded was the locknut.
well...240.4(A)(2) would require that locknut to be bonded if the enclosure is nonmetallic :D
 