So another related question. So if a grounding bushing is required would it HAVE to be at every box, enclosure etc. the conduit "terminates" at or possibly only at specific point along the run? So some locations along the same run could have a regular bushing and some could have a grounding?
]
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So another related question. So if a grounding bushing is required would it HAVE to be at every box, enclosure etc. the conduit "terminates" at or possibly only at specific point along the run? So some locations along the same run could have a regular bushing and some could have a grounding?
]
Grounding bushings are rarely required. Do you have a specific type of installation that requires them?
 
So another related question. So if a grounding bushing is required would it HAVE to be at every box, enclosure etc. the conduit "terminates" at or possibly only at specific point along the run? So some locations along the same run could have a regular bushing and some could have a grounding?
]
Not necessarily every box. Think of a MIGB as possibly being needed at a connector/ box/cabinet, like Larry said depending on the voltage, if it's a service, and if it's got concentrics. It may be needed at some terminations and not others - unless it's a service then you need one at every connector (well some additional bonding, could be a BL or wedge).
 

kwired

Electron manager
Location
NE Nebraska
So another related question. So if a grounding bushing is required would it HAVE to be at every box, enclosure etc. the conduit "terminates" at or possibly only at specific point along the run? So some locations along the same run could have a regular bushing and some could have a grounding?
]
The intent of such item is for when there is or possibly could be an impaired bond by a regular locknut for various reasons, it just gives an alternate path that is more assured will be a sufficient path.

A metal raceway entry into a non metallic enclosure or where there is no enclosure wall say bottomless gear or where transitioning from metal raceway to open conductors also would be a place where a bonding bushing very well might be used
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Why does it not make sense? The locknut on the raceway or EMT connector makes the metal to metal connection to the box.
Yes. Is it a concentric KO one that's partially imprinted to be knocked out? So whether you knock out your own holes or have the concentric you still need lock nuts
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes. Is it a concentric KO one that's partially imprinted to be knocked out? So whether you knock out your own holes or have the concentric you still need lock nuts
Yes you'll need locknuts. Also if the voltage is 208Y/120 or 120/240 even with concentric KO's bonding bushings would only be required on service raceways.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Yes you'll need locknuts. Also if the voltage is 208Y/120 or 120/240 even with concentric KO's bonding bushings would only be required on service raceways.
Yes but I'm referring to the grounding bushing. Did you say that whether the ko's are concentric or punched out yourself makes a difference if a grounding bushing is required??
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Would you need a seprate bushing( whichever type) for this hub?
No. The insulated throat is all that's required.

Yes but I'm referring to the grounding bushing. Did you say that whether the ko's are concentric or punched out yourself makes a difference if a grounding bushing is required??
What voltage are you referring to? For less than 250 volts to ground a bonding bushing is not required even with concentric or eccentric KO's.
 