Code used to required bushings on any conduit an 1 1/4" and larger, however the code has changed requiring any conduit containing a #_____________ wire or larger to have a bushing. Insert correct wire size:
Back when only the dinosaurs and I worked, the use of a bushing was based on the conduit size. It was changed to wire size.
Thanks for the info but i did look at 300.4 (G) and does not help.. that question is just like that in a on line test for a company, but is ok Thanks anyway
300.4(G) Insulated Fittings. Where raceways contain 4 AWG or larger insulated circuit conductors and these conductors enter a cabinet, box, enclosure, or raceway, the conductors shall be protected by a substantial fitting providing a smoothly rounded insulating surface, unless the conductors are separated from the fitting or raceway by substantial insulating material that is securely fastened in place.
Exception: Where threaded hubs or bosses that are an integral part of a cabinet, box, enclosure, or raceway provide a smoothly rounded or flared entry for conductors.
Conduit bushings constructed wholly of insulating material shall not be used to secure a fitting or raceway. The insulating fitting or insulating material shall have a temperature rating not less than the insulation temperature rating of the installed conductors.
I've heard that and was taught that in apprentice school but does anyone have a reference from an old code book?
Why doesn't 300.4(G) help to answer the question? The wire size is mentioned in that section #4 AWG or larger. :?
1951 NEC, 318, #4 or larger conductors require bushings. I will look in 1940 later.
Why doesn't 300.4(G) help to answer the question? The wire size is mentioned in that section #4 AWG or larger. :?
Not sure where the 1.25" raceway comes from but take a look at 300.4(G).