Busway Feeder size
John Dundon
CT
I am currently feeding a 480V 3-wire 400 amp busway with set of parallel 3/0 THHN conductors which gives me a total ampacity of 400A @ 75 deg. The busway is providing power to various CNC machines. Do I have enough copper?
Baring some unforeseen element such as ambient or voltage drop, I see no problem.
First timer and I like this forum.
Thank you for the input. I had one of those over thinking it moments. I was thinking that because the loads of this busway had motors that I would need to be 125% for the feeders to the buss. I will do that calc from the busheads to each machine.:thumbsup:
The Busway is part of the feeder so if the busway is 400A, then the conduit/wire should be 400A