R rmonroe Member Mar 9, 2015 #1 We have 2 busway system in our plant. One is 3-Wire and a 4-Wire. Can I use the bus-plugs from the three wire on the four wire system? Is their any code in regards to this topic? rmonroe
We have 2 busway system in our plant. One is 3-Wire and a 4-Wire. Can I use the bus-plugs from the three wire on the four wire system? Is their any code in regards to this topic? rmonroe
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems Mar 9, 2015 #2 The answer is likely manufacturer dependent. For example, Square D plugs, up to 200A, will work on busway with or without a neutral. It is the type of plug-in jaw that is the deciding factor.
The answer is likely manufacturer dependent. For example, Square D plugs, up to 200A, will work on busway with or without a neutral. It is the type of plug-in jaw that is the deciding factor.
R rmonroe Member Mar 9, 2015 #3 jim dungar said: The answer is likely manufacturer dependent. For example, Square D plugs, up to 200A, will work on busway with or without a neutral. It is the type of plug-in jaw that is the deciding factor. Click to expand... Thanks Jim
jim dungar said: The answer is likely manufacturer dependent. For example, Square D plugs, up to 200A, will work on busway with or without a neutral. It is the type of plug-in jaw that is the deciding factor. Click to expand... Thanks Jim