brian john
- Kilmarnock, Va
- Retired after 52 years in the trade.
Over the years I have seen numerous problems made with busway, I am surprised by the number of contractors and end users that do not take the basic steps to insure a problem free installation.
In the last week I have been involved in two busway incidents, the first was water and the busway was de-energized and bypasses, in the second incident the 4000 amp busway was dripped on for a period of time and finally vaporized. While busway is an excellent way for distribution there are some draw backs and water is the number one enemy of busway.
In all the time I have been involved with electrical testing faulted busway ranks way above faulty cable as the number one feeder fault.
1. Busway when installed should be damned at all floors to prevent the intrusion of water.
2. Horizontal runs of busway should be shielded where water pipes, ducts that might condensate and expansion joints cross paths.
I have been involved in several instances of new installations where the contractor did not follow a few basic rules and the project took a monetary hit.
1. Upon the receipt busway should be numbered and meggered as it comes off the truck.
2. Stored in a dry location on 4x4 and COVERED.
3. Installed only after the building is sealed.
4. Each piece should be meggered as it goes up.
5. After installation of a new piece the entire length should be meggered.
6. Care should be taken to run the busway as straight and/or level as possible as angle bends at joints put undo pressure on the couplings and the plastic separators/insulators.
7. Upon completion the busway should be meggered and documented, all parties involved should be notified the busway is acceptable for use.
8. Prior to energizing for the first time the busway should be meggered and the original report should be checked for comparison of readings.
9. Should there be any water issues on the job megger the busway immediately and notify all parties of any issues.
10. During construction the GFP should be left set at 100 Instantaneous or minimum delay.
11. After construction as the GFP should be set to pick-up and delay as determined by the coordination study.