NEC 2014 110.26(C)(3) Personnel Doors. Where equipment rated 800 A or more
that contains overcurrent devices, switching devices, or control
devices is installed and there is a personnel door(s) intended
for entrance to and egress from the working space less than
7.6 m (25 ft) from the nearest edge of t he working space, the
door(s) shall open in the direction of egress and be equipped
with listed panic hardware.
scenario: 3000 amp rated vertical busway thru 4 floors. Maximum 600 amp fused disconnect connected to busway on 2nd & each floor up in dedicated electrical rooms. Egress door 12' away with clear path from equipment in each room. Will the egress door be required to meet the 800 amp or more restrictions because we have a 3000 amp busway going thru the room? or should it be interpreted as "600 amp disconnect" being less than the prescribed 800 amps or more? and allowing the egress door to lesser restrictions.
that contains overcurrent devices, switching devices, or control
devices is installed and there is a personnel door(s) intended
for entrance to and egress from the working space less than
7.6 m (25 ft) from the nearest edge of t he working space, the
door(s) shall open in the direction of egress and be equipped
with listed panic hardware.
scenario: 3000 amp rated vertical busway thru 4 floors. Maximum 600 amp fused disconnect connected to busway on 2nd & each floor up in dedicated electrical rooms. Egress door 12' away with clear path from equipment in each room. Will the egress door be required to meet the 800 amp or more restrictions because we have a 3000 amp busway going thru the room? or should it be interpreted as "600 amp disconnect" being less than the prescribed 800 amps or more? and allowing the egress door to lesser restrictions.