We lost a lot of member's profile with the change in the Forum, would you please update your profile to include your occupation and general location?The factory leads are too short. Is it an acceptable practice to But Splice Leads in a ceiling fan down rod?
It isn't compliant.The factory leads are too short. Is it an acceptable practice to But Splice Leads in a ceiling fan down rod?
But is done all the time! LOL!It isn't compliant.
Just curious, what would you cite as the violation? Maybe not accessible?It isn't compliant.
never had an issue with butt splices as long as they are done right and not in a location they shouldn't be.I hate those things, I find way too many that are the problem when I'm troubleshooting. If it was mine, I'd solder ind heat shrink
as long as they are done right and not in a location they shouldn't be.
this is what I have done in those cases as wellI hate those things, I find way too many that are the problem when I'm troubleshooting. If it was mine, I'd solder ind heat shrink
300.15Just curious, what would you cite as the violation? Maybe not accessible?
300.15 Boxes, Conduit Bodies, or Fittings — Where Required.
A box shall be installed at each outlet and switch point for
concealed knob-and-tube wiring.
Fittings and connectors shall be used only with the specific
wiring methods for which they are designed and listed.
Where the wiring method is conduit, tubing, Type AC cable,
Type MC cable, Type MI cable, nonmetallic-sheathed cable, or
other cables, a box or conduit body shall be installed at each
conductor splice point, outlet point, switch point, junction
point, termination point, or pull point, unless otherwise
permitted in 300.15(A) through (L).
I wouldn't think a downrod would be considered RMC.300.15
Rmc 344.56 Splices and Taps. Splices and taps shall be made in
accordance with 300.15.
I don't think that rule would even allow it in rmc right?I wouldn't think a downrod would be considered RMC.
Well the rod is a conduit of some sort so 300.15 alone deals with that.I wouldn't think a downrod would be considered RMC.