butt splice on se cable

Status
Not open for further replies.

Hacker71

Member
Is it now legal to splice entrance cable between meter can and main breaker? if so are their any particulars I need to be aware of (i.e. type of splice, enclosure needed, etc.)?

Thanks
 
Thanks billy...I referred to that section, and its further references...would like to use a PVC 6x6 box with approved butt splices for the 2/0 CU and heat shrink on the splices...
 
Hacker71 said:
would like to use a PVC 6x6 box with approved butt splices for the 2/0 CU and heat shrink on the splices...

A 6" x 6" for six 2/0 CUs?

Are you built like "The Rock"?

If it was me I would not even think of a box less than 12" x 12" x 4"
 
Just curious, if the distance between the meter pan and the breaker panel has to be "the shortest distance possible" , why not replace the entire length of cable ? I know I don't have all the particulars of the job but it would seem to be easier to replace the cable than it would to mount a 6 x 6 box with w/p connectors and butt splice it in the box.

BTW, NSI and Polaris make insulated butt splices. I would look into one of those before I used heat shrink and std. butt splices. A few $$ more but well worth it.
 