Buzzing contactor

Status
Not open for further replies.

SAP

Senior Member
Location
Fresno Ca
We have a office building with a six pole GE contactor with timer and bypass keyed switch, for lighting ,timer comes on contactor close, customer does not like the little buzzing, I'm gonna switch the contactor to NC during the day when timer comes on contactor opens after hr, I'm thinking how would the bypass switch work,
 
We have a office building with a six pole GE contactor with timer and bypass keyed switch, for lighting ,timer comes on contactor close, customer does not like the little buzzing, I'm gonna switch the contactor to NC during the day when timer comes on contactor opens after hr, I'm thinking how would the bypass switch work,

You would have to reverse the bypass switch as well. But I think a better option would be to just change the the contactor to a mechanically held type. I seem recall, some of the GE sfuff can be converted to mechanically held in the field.
 
Buzzing contactor points me to dirty components or not properly installed coils.

Check out the aramture and shading coil many times it is metal shavings from drilling in the panel to secure the components.
 
I think a better option would be to just change the the contactor to a mechanically held type.

I agree with Texie, a mechanically held contactor is a better design. It will last longer and there won't be any buzzing.

Another vote for mechanically held, it is the correct choice for lighting loads.

Yeah you might be able to make the one you have quiet but it will start buzzing again.
 
Another vote for mechanically held, it is the correct choice for lighting loads.

Yeah you might be able to make the one you have quiet but it will start buzzing again.

Wonder if this is why we've had 2 of these fail in the past 2 months? We are using square d up to 12 contacts per box, electrically held. 277v coils.
 